Delta-Delta Ground Fault

Delta-Delta Ground Fault

Delta-Delta Ground Fault

(OP)
Hi, İs delta-delta connection exposed to ground faults? İ figure it is not. İf not how do we dedect these faults?  

RE: Delta-Delta Ground Fault

Ungrounded systems are a bad idea. That said, grounds may be detected on a floating system with voltage monitoring. Delta systems may be grounded with a zig-zag transformer or with a wye/delta transformer.  

Bill
--------------------
"Why not the best?"
Jimmy Carter