Why KWHr on meters instead of KVAHr?
Loads can be resistive, inductive or capacitive. However, when we look at the meters it only indicates energy cosumed in KWHr. Are we ignoring the reactive power in billing?
RE: Why KWHr on meters instead of KVAHr?
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
Gunnar Englund
www.gke.org
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
I am guessing a poor powerfactor load equates to high current consumption which equates to higher bills.
eg: If the average power factor for a month was 755 then a penalty of 0.9 - 0.75 or 15% would be applied to the KWHr consumption charges.
Now there are much more punative formulas and some countries charge for any amount of KVARHr consumption, either leading or lagging.
As has been mentioned, KVAR metering and PF penalties were applied to large commercial and industrial users.
Bill
"Why not the best?"
Jimmy Carter
It does, of course take money to build lines and equipment to carry kvar and fuel to generate the kWh from losses caused by kvar.