Minimum steel in pier

Minimum steel in pier

Minimum steel in pier

(OP)
I was asked to review a reinforced concrete footing/pier which supports a steel canopy.  After review the footing meets code and is more than adequate, but the pier has less than the code required long. steel for columns (<0.3%).  The pier meets the criteria for mass concrete dimensionally, but with anticipated lateral loads, the resultant is outside the middle third.

The issue is it is already constructed including final paving above.  I am leaning toward saying to excavate and place mass concrete around the pier.

Any thoughts?  Thanks in advance.

RE: Minimum steel in pier

what are the dimensions of the pier?

RE: Minimum steel in pier

(OP)
Sorry,  the pier is 16"x16" and 24" high with a 5kip lateral load.  the reinforcing is four #4 bars.

A second pier is slightly larger at 20"x20" and 24" high. with the same reinforcing and load.

RE: Minimum steel in pier

I don't believe that you need to meet minimum column reinforcement requirements (1%) for piers, but you do neet to meet requirements for pedestal reinforcement dowels into the footing (0.5%) - ACI 15.8.2.1.

That's just my interpretation.

RE: Minimum steel in pier

Quote (llamallama):

but the pier has less than the code required long. steel for columns (<0.3%)

Where is this code provision contained?  ACI 318 says, in section 1.1.5, that it does not apply to portions of drilled piers embedded in the ground (except for certain seismic situations).

I'm not saying the design isn't suspect; rather, the minimum requirement you're referencing may not apply.

RE: Minimum steel in pier

(OP)
Thanks for the replies.  This was an excavated/formed pier, so I didn't think section 1.1.5 applied.  I've always assumed that was for earth-formed piers (i.e. augered holes w/ rebar cage) and not formed piers.

RE: Minimum steel in pier

Not a foundation pier - use ACI 318 - Compression member design - Minimum steel = 0.5% for oversized column.  Bad day for somebody.

RE: Minimum steel in pier

My interpretation is that this pier does not have the minimum required area of steel (0.5%), and should therefore be checked as an unreinforced pier.

Phi*Mn for the 16" X 16" pier = 10.8 KF (assuming f'c = 4,000 psi), so if the 5 kip lateral load is an ultimate load, you are OK (Mu = 10 KF).

DaveAtkins

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources