sprinklers in skylights
sprinklers in skylights
(OP)
I have a question about little skylights in warehouse area. In warehouse area are ESFR K200 sprinklers. Some of skylights them are equipped with smoke vent feature.
The skylights are 3,75m2 area (1,5mx2,5m) and are slightly more than 3,0m2 from NFPA13 edition 2010 point 8.5.7.1. The distance beetwen skylights are more than 3,0m.
We think, that the sprinklers will be ommited from this skylights. What do you think about it,Is it correct?
The skylights are 3,75m2 area (1,5mx2,5m) and are slightly more than 3,0m2 from NFPA13 edition 2010 point 8.5.7.1. The distance beetwen skylights are more than 3,0m.
We think, that the sprinklers will be ommited from this skylights. What do you think about it,Is it correct?





RE: sprinklers in skylights
RE: sprinklers in skylights
Have you considered this in your design?
RE: sprinklers in skylights
RE: sprinklers in skylights
RE: sprinklers in skylights
RE: sprinklers in skylights
RE: sprinklers in skylights
are you meeting 8.12.2.3?? section
can it meet ceiling pocket section??
RE: sprinklers in skylights
RE: sprinklers in skylights
RE: sprinklers in skylights
So could you say if the skylight was proven to be limited combustible it would qualify as a pocket ????
RE: sprinklers in skylights
RE: sprinklers in skylights