Asbestos' (or Asbestos-Cement's) Corrosion Resistance agaist Salt
Asbestos' (or Asbestos-Cement's) Corrosion Resistance agaist Salt
(OP)
Hello,
I was wondering if somebody can help me out with a question I have with concerns to Asbestos. Would anybody have a Chart that indicates the Corrosion Resistance of Asbestos (or Asbestos-Cement) against Salt? If so, I would greatly it if you could send me a copy or direct to me where I can get it. I am presently working on a design that requires we take a look at this detail.
Thank you.
I was wondering if somebody can help me out with a question I have with concerns to Asbestos. Would anybody have a Chart that indicates the Corrosion Resistance of Asbestos (or Asbestos-Cement) against Salt? If so, I would greatly it if you could send me a copy or direct to me where I can get it. I am presently working on a design that requires we take a look at this detail.
Thank you.





RE: Asbestos' (or Asbestos-Cement's) Corrosion Resistance agaist Salt
We have pumped brackish and saltwater through Transite, ACM, pipe for over 40 years with no problems.
You might want to check out the AWWA site since there is a lot of this pipe in use today. You will not find very many references to ACM from US companies due to the association of Asbestos with lung diseases.
Here is just one specification that gives data for ACM pipe plus a link to the mfg website.
http://www.logard.com/Pdf/catalogueAnglais.pdf
http://www.logard.com/en/home.aspx