Do we require sprinkler in utilidor
our utilidor constructed with concrete and considered as non combustable construction.
and as per NFPA 13 section 8.15.1.2.2 the concealed sapce with limited access and not permitting occupancy is expemted from sprinkler
please advice
our utilidor constructed with concrete and considered as non combustable construction.
and as per NFPA 13 section 8.15.1.2.2 the concealed sapce with limited access and not permitting occupancy is expemted from sprinkler
please advice





RE: Sprinkler in Utildor
RE: Sprinkler in Utildor
RE: Sprinkler in Utildor
RE: Sprinkler in Utildor
Examples:
Full size man door with no lock, definitely not limited access.
Access hatch/panel attached with screws/bolts, definitely IS limited.
Everything else in between is subject to interpretation, with the goal being that people don't or cannot use the area for storage.
Keep in mind you are using the section of the code that is basically written for above-the-ceiling space.. So it comes down to what kind of mood the AHJ is in that day. If you put a permanent no storage on order of fire dept. sign up inside the space, and put in a less than full size door which locks that should satisfy the crustiest of AHJs.
RE: Sprinkler in Utildor