transformer inrush for distributed transformers
transformer inrush for distributed transformers
(OP)
I work for municipal that distributes electrical power. Voltage is 12,470 phase-to-phase. Understanding/calculating transformer inrush for a single transformer is pretty straightforward -- 12X rated load for 0.1 second.
We have fused sections of distribution where the connected transformer kVA varies, but, for example lets assume we have 480 kVA connected over a section of 2 miles. We would probably use 4/0 aluminum primary. Lets say the 480 kVA is 8-50 kVAs and 1-80 kVA and is distributed across the miles.
Would the inrush still be 12X 480kVA at 0.1 second? If not, how much less would it be? And, why would it be less?
I also believe inrush at .01 second is about 25X rated load.
We have fused sections of distribution where the connected transformer kVA varies, but, for example lets assume we have 480 kVA connected over a section of 2 miles. We would probably use 4/0 aluminum primary. Lets say the 480 kVA is 8-50 kVAs and 1-80 kVA and is distributed across the miles.
Would the inrush still be 12X 480kVA at 0.1 second? If not, how much less would it be? And, why would it be less?
I also believe inrush at .01 second is about 25X rated load.






RE: transformer inrush for distributed transformers
Generally a 4/0 ckt would be under the sub breaker or a line OCB.
RE: transformer inrush for distributed transformers
We are thinking we could put a relay on a section that is likely to operate soon and take a real meaasurement. However, maybe someone has already some knowledge regarding this issue.
RE: transformer inrush for distributed transformers
I may have confused you. When I said utilities use 150% of FLA, I meant that is for the individual transformers. Your line fuses are determined by a coordination study. You use the max size fuse that will coordinate with the sub breaker. How were your guide lines determined?
RE: transformer inrush for distributed transformers
Our Max KVA for a fuse has been based upon the assumption that a distributed set of transformers has the same inrush current as one equivalent big transformer. Intuitively, this does not seem to be true. The concern is that if the fuse is not sized for the inrush current, when you close it back in, it will operate again on inrush and we would be "up the proverbial creek without a paddle."
Actually, we would have to take time to sectionalize the section and close it back in in pieces.
RE: transformer inrush for distributed transformers