Conc. Wall Dowel Bend Direction

Conc. Wall Dowel Bend Direction

Conc. Wall Dowel Bend Direction

(OP)
For a concrete wall bending transversely, does the direction of the dowel hook of the vertical wall reinforcing bar into the footing bends.  Whether it bends towards each other or away from each other, in a wall with two layers of reinforcing.  

RE: Conc. Wall Dowel Bend Direction

I wouldn't think so...how does it know which way its developed when tension is on the bar? The hook just needs to be developed properly in my mind.  

RE: Conc. Wall Dowel Bend Direction

Its somewhat a personal preference, but I like them facing each other. It just seems stronger to have the bend of the hook closer to the comprssion region of the concrete rather than the slab.

RE: Conc. Wall Dowel Bend Direction

Check out the attached link.  The CRSI (US) article on page 14 has what you are looking for.

There is also a requirements for hook orientation in Chapter 21, if required.

RE: Conc. Wall Dowel Bend Direction

(OP)
Yes, thank you Galambos!  I knew I saw that somewhere before but I could not find it.  I actually read it in another publication.  I've been looking for it for the past two years.

RE: Conc. Wall Dowel Bend Direction

Galambos, thanks for that! That is counter-intuitive and not what most of us were probably taught. I don't do much concrete design but plenty of retaining walls where that detail will be put to use.

Thanks,
Andrew Kester, PE
Florida

RE: Conc. Wall Dowel Bend Direction

Does this apply to all T-joints or is there a caveat based on the thickness of each portion of the T?

I have seen column starter dowels are typically hooked outward. ACI SP-66 also has a diagram showing something similar.

Is it recommended for all column starter dowels to be hooked facing each other as well?

RE: Conc. Wall Dowel Bend Direction

slickdeals
Way out of my area of expertise, but I think this applies to hooked bars that will be loaded in TENSION...

RE: Conc. Wall Dowel Bend Direction

You can have a column with significant moment at the base which will put the reinforcing in tension.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources