Solid State Starting and Starting Torque
Solid State Starting and Starting Torque
(OP)
Hello everyone. I am new to this place and I look forward to any help that you could lend me.
I have a Sprecher Schuh PCS-480-600V soft starter for a 300 HP well motor. The soft starter uses dip switches to obtain certain settings like current-limit start and soft starting capabilities.
As for soft starting you can limit the initial torque to a percentage of Locked Rotor Torque (15, 25, 35, and 65) and with Current Limit starting you can limit the current to a percentage of FLA (150, 250, 350, and 450).
You can also set a soft start ramp time (2, 5, 10, 15, 20, 25 and 30).
My question is: What would be the minimum initial torque/initial current setting to be able to properly start the motor without overheating?
If more information is needed I will get it for you.
I have attached a pdf of the soft starter installation guide if that will help.
Thanks for any help y'all could give me.
I have a Sprecher Schuh PCS-480-600V soft starter for a 300 HP well motor. The soft starter uses dip switches to obtain certain settings like current-limit start and soft starting capabilities.
As for soft starting you can limit the initial torque to a percentage of Locked Rotor Torque (15, 25, 35, and 65) and with Current Limit starting you can limit the current to a percentage of FLA (150, 250, 350, and 450).
You can also set a soft start ramp time (2, 5, 10, 15, 20, 25 and 30).
My question is: What would be the minimum initial torque/initial current setting to be able to properly start the motor without overheating?
If more information is needed I will get it for you.
I have attached a pdf of the soft starter installation guide if that will help.
Thanks for any help y'all could give me.





RE: Solid State Starting and Starting Torque
If this is the case for your installation, you would want settings that achieve the fastest possible start while limiting the voltage drop on the line to acceptable levels. In my opinion the most direct way to do this would be using 'current limit' starting. You can determine the settings by trial and error or by estimating the value of voltage drop for a given inrush current based on the upstream conductor sizing, length of run, and size of the upstream transformer.
If your soft start is being used for some other reason such as limiting accelerating torque due to mechanical limits in the system, then 'torque limit' starting may be a more intuitive way to do this. Even so, you would still want to achieve the fastest start possible without exceeding the mechanical torque limit and breaking something.
RE: Solid State Starting and Starting Torque
In general, due to the reduced torques and currents, you can accelerate up to speed in as long a time as you please. For NEMA size motors, the motor thermal limits will rarely be exceeded. It doesn't hurt to keep those thermal limits in mind, however, particularly for very large motors and very long accel times. In these larger motors, the limits will be specific to the particular motor and you will need to consult with the manufacturer for help.
RE: Solid State Starting and Starting Torque
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Solid State Starting and Starting Torque
From my research on the motor and the pump, (Its a 300 HP vertical induction motor with a Floway 14 DKM 8 stage pump) it looks as if by reducing the current limit/torque limit this reduces the Speed-Torque curve of the motor. And from what I understand the Speed-Torque curve of the pump cannot exceed the curve for the motor before it reaches the rated speed of 1770 rpm. If this happens the motor will never reach its rated speed.
Does this sound correct? If the motor never reaches its rated speed it could possible create a thermal overload. Is this correct as well?
The whole purpose of this is that I am sizing a diesel generator for the site. If I can reduce the current limit/torque limit on the soft starter, I can reduce the size of the generator, which is optimal.
RE: Solid State Starting and Starting Torque
At least with voltage control, under near-stall conditions, the rising voltage will eventually force progression thru the stalling point up to full speed.
If you require more current to get thru the stall point than the source can provide, you've got a fundamental problem with sizing that needs a different solution than softstarting.
RE: Solid State Starting and Starting Torque