Bearing Capacity Formulae For Clays
Assuming phi = o and saturated clay soil.
If a square foundation is at a depth of D, do we need to put bouyancy unit weight of soil to calculate(gama.D.Nq component?
q = 5.5 C Nc + (gama).D.Nq
RE: Bearing Capacity Formulae For Clays
when using phi=0 ground water table is not an issue.  Use your total unit weights. That said, I'd assume no depth of burial and just use 5.5*Su.  Su is the undrained shear strength, which is technically different from cohesion.
Don't forget your safety factor - typically taken as 3.0.
f-d
¡papá gordo ain't no madre flaca!
So does it mean that if the square footing would be at a depth of D or on the ground surface, it has no effect on the ultimate bearing capacity.  Sorry, I may miss something here.
No the depth of burial will factor into the design if you want it to.  I just don't.  Never know when something is going to get dug up, or a slab on grade replaced, or something else. . .
f-d
Dear Fattad
Ok if I decided to take into account the depth of overburden in clay materials, should it be (gama)'D or (gama)D?  Thank you again.
Me - I just use 2xSu and leave it at that - close enough.  Then check the anticipated settlement and adjust your allowable bearing pressures from there.
Again, I agree with BigH - exactly what I do also.
Regarding the qusetion of how to handle the depth of burial, if you are looking at undrained conditions, you have to use total loads.  So, that'd be gammaD.
f-d