(OP)
Hello All

Usually they use 400 cfm per ton, but this needs the delta T between suply ait temperature and cooling set point to be about 27F, so if the set point was 75F then the suply air has to ba about 48F
I know the suply air usualy is about 55 to 58 F
shall we have to go with this rule of thumb 400cfm/ton or go with program result?
Thanks

RE: cfm

You're leaving out the latent heat removal that's done at the cooling coil.  Not all of the capacity goes into reducing dry bulb temperature.

Look at a psych chart and a typical coil curve.

Good on ya,

Goober Dave

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources