Does anyone see an issue with supplying a receptacle rated for 50A, 125/250V, 3-pole, 4-wire with a 50A 120/208, 3phase, 4-wire feeder?

RE: Question regarding feeder to receptacle

I assume you are using a NEMA receptacle 14-50R, (3 pole, 4 wire 250/125V) which is designed for one ground, two hot leads and one common or neutral lead.

The 208/120 3 phase , 4-wire system has three hots, one neutral and no ground. (NEMA 18-50R plug).

You will end up putting 120V on a pin that is designed for the grounded neutral conductor.  That could be dangerous to someone in the future.  It might be safe, depending on how the plug connected equipment is connected, but it probably isn't.

Best to use the correct plug if you need 3-phase power.

But if you only need single phase power, wire the plug with two hots, a neutral and a ground.  The only difference will be the hot pins will supply 208 V instead of 240V.  Hot to neutral will still be 120V and the ground will be connected.

RE: Question regarding feeder to receptacle

If you are using 2 hots, neutral and ground to supply a single phase range or similar appliance (via a NEMA 14-50R or similar) I would and have done that.

If in fact you intend to supply a "120/208 3 phase" (3 hots and a ground) load via such a receptacle, I have several reservations, the most significant- where do you put the 3rd hot? Use what would normally be the neutral terminal for a 120 volt lead? Not me.

There are several other NEMA receptacles that are more suitable, even a twistlock 4 pole 5 wire configuration if you want to run both neutral and ground to your receptacle; NEMA L21-50R and L21-50P respectively.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources