Testing of Intrinsically safe bariers
I do not have a lot of experience with I.S. Barriers.
My question is fairly simple.
Should you test I.S. Barrier?
How frequently should you test them?
What is the testing procedure for one?
Thank you for all your responses.
Sincerely,
Dan
RE: Testing of Intrinsically safe bariers
9.5.5 Maintenance
No special maintenance of intrinsically safe systems is required. Once a year the barriers should be checked to ensure that the connections are tight, the ground wiring has less then one ohm of resistance, and the barriers are free from moisture and dirt. Check the panel and conduits for separation and identification of the intrinsically safe wiring. Never test the barrier with an ohmmeter or other test instrument while it is connected in the circuit (see figure 11). This bypasses the barrier and could induce voltages into the intrinsically safe wiring.
entire I/S article here:
http://www.iaei.org/magazine/?p=3053
Yep.  No testing is needed.  Just installation checks.  I once showed up to a sterilization plant to install new controls.  They had all the IS wiring sharing a raceway with 480Vac..
Keith Cress
oops...
Thank you for your responses.
Article from IAEI is exactly what I was looking for.
Once again, Thank you.