%IMPEDANCE CALCULATION OF TRANSFORMER
Dear Sir
Please let us know what is the relation between %impedance ,BIL & short circuit current of the transformer
RE: %IMPEDANCE CALCULATION OF TRANSFORMER
i want to know the relation between impedance and short circuit current.
if possible kindly send me the formula
Where:
Tx FLA = the full amps at the base transformer rating, and
Zpu = per unit impedance of the tranformer= 100 x %Z.
Example: short circuit through a transformer with 10%Z will be 10 times its full load amps, assuming it is fed by an infinite source.
Bill
"Why not the best?"
Jimmy Carter
If you're talking big transformers at high transmission voltages it can be a reasonable assumption. If you're talking small transformers connected into the distribution system it may not be such a good assumption.
"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla
"If you're talking big transformers at high transmission voltages it can be a reasonable assumption. If you're talking small transformers connected into the distribution system it may not be such a good assumption. "
True but many utilities will use this when giving a fault current value to a customer.
Thanks for the correction.
Isc = FLA /Zpu = (FLA x 100%)/%Z
ithink its good for us