Plywood Gusset Plates
Can anyone direct me to design information on the use of plywood gussets in a truss type element?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: Plywood Gusset Plates
In short, determine the shear load and design using 1/2" nominal plywood thickness with enough fasteners to handle the shear as well as any safety factor needed.
Current codes use truss fasteners (metal) and the provisions for plywood gussets are obscure. There is a lot of information with regard to maximum stresses in plywood and some references to gussets such that the gusset can be sized, but the nailing requirements are obscure and are not clear.
Another source is the Council of Forest Industries of B.C. (COFI). COFI has a lot of plywood literature, which was free (in 1986) the phone number in 1986 was (604) 684-0211.
I recommend telephoning the Canadian Wood Council for advice, the CWC is very helpful and may better direct you. CWC tel: (613) 731-7899 or toll free 1-800-463-5091.
For fastening requirements I recommend the Canadian Wood Council (CWC) book "Wood Design Manual". Section 7.2 of the manual"Nails and Spikes" provides design guidelines for fastening of the gusset.
Essentially the design process is two fold. First size the gusset according to strength requirements. Then using the CWC manual determine the nailing requirements. The nailing requirements are based on the minimum thickness of plywood, nails, and truss member grade. The Wood Design Manual will provide all the information required for designing wood trusses with either metal truss plates or plywood gussets.