blow out fuses of capasitor bank

blow out fuses of capasitor bank

blow out fuses of capasitor bank

(OP)
Hai all...i would apriciate all of you  to explain of me..
may question: could u tell me what main cused of fuses capacitor bank on distribution line burn out..( capacitor bank 300KVAR) system 13.8KV
thnks before

RE: blow out fuses of capasitor bank

About the only thing that causes fuses to blow is too much current.  Not enough information to figure out why you might be seeing too much current.  What kind of damage are you seeing on your capacitors?

RE: blow out fuses of capasitor bank

(OP)
How about The Harmonics on distribution lines it's culd be effect of blow -out fuses of capacitor bank unit
and why the curent is too much at capacitor bank..?

thanks..for your help

RE: blow out fuses of capasitor bank

What fuse rating are you using?

Are these switched or fixed capacitor banks?

RE: blow out fuses of capasitor bank

Are the capacitors individually fused? Are you blowing the main fuses? Is it the same one all of the time? Is the capacitor bank enclosed, outdoors? We have had birds, raccoons and cats step across our old 410kvar 23kv cap bank in our outdoor substaion. You should see what that does to a small animal--not pretty. We have since replaced the old bank with a fully enclosed one. What about lightning strikes, transients? What kind of load are you feeding? We have a fixed bank feeding an electric arc furnace. These can at times single phase as well as other things that can demand above full load current for brief periods.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources