Hi guys,

Do either of you have a good spec for testing 11kV indoor switchgear?

I am extending an 6.6kV SB for our customer by adding a couple of CBs.

I was going to recommend the following tests but would welcome any comments and suggestions:

1.    Ducter new bus connections
2.    5kV Megger
3.    Primary and secondary injection tests

Was also considering Hi-pot but I'm not sure if that is really used anymore for MV switchgear?
 

RE: 11kW Switchgear Testing

Yep, NETA specs, which are now an ANSI standard. You don;t really need to list them all, just put "Tesing IAW ANSI/NETA ATS", the testing company will then have to do all of the required tests.

THere are a few optional tests in the specs so you may want to clarify if you want those done or not.  

RE: 11kW Switchgear Testing

If you are in an IEC country IEC 60694:Common specifications
for high-voltage switchgear and controlgear standards section lists the routine tests which included dielctric (high voltage) testing.

Primary and secondary current injection will verify the CT/protection relay scheme

 

RE: 11kW Switchgear Testing

Primary and secondary current injection is the term you want to use for medium voltage testing

On medium voltage switchgear, ct testing is usually performed with the voltage method.


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources