How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
(OP)
As the title states, I've been having trouble figuring out how to run a certain large dryer for corn and rice due to the available supply in our locality.
The dryer is a modular equipment that runs at a total of 30-hp and requires a 440V, 3-phase supply. The only available supply is 230V, single phase.
A friend suggested running it by connecting the system as follows: supply-transformer-phase converter-dryer OR supply-phase converter-3ph transformer-dryer.
Costing aside, will this be a feasible option? Are there any other cheaper ways to run the dryer?
I will greatly appreciate your help on this matter. Thank you.
The dryer is a modular equipment that runs at a total of 30-hp and requires a 440V, 3-phase supply. The only available supply is 230V, single phase.
A friend suggested running it by connecting the system as follows: supply-transformer-phase converter-dryer OR supply-phase converter-3ph transformer-dryer.
Costing aside, will this be a feasible option? Are there any other cheaper ways to run the dryer?
I will greatly appreciate your help on this matter. Thank you.





RE: How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
As for cheaper or not, you need to compare the costs. If high tech maintenance and service/troubleshooting is an issue in the remote area, I would stay with low tech but robust phase converters.
Regardless, 30 HP is too much for a single phase 230V supply, you need to make sure that service transformer is big enough. Work with your utility co.
Rafiq Bulsara
http://www.srengineersct.com
RE: How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
Your options:
1) Transformer + Rotary Phase Converter = very inefficient but possible to run multiple motors from one large system. But you may have trouble starting the "idler" for a single system that size from that 1 phase supply.
2) Transformer + Static Phase Adder = More efficient, less flexible in terms of it's ability to start and stop multiple downstream motors, still does nothing to soft start the load so still may be a problem for that 1 phase supply at that size. If the loads can stagger-start, maybe you can use multiple Static Phase Adders to get around that.
3) Transformer(s) + VFDs. This is the best suggestion I can give you without knowing a whole lot more than what you have provided. Evaluate the motor power requirements for each "module" and use a transformer to go from 230 to 460V single phase, then put an appropriate 480V rated VFD for each of the motors. Each VFD will need to be twice the size of the motor, i.e. if you have a 5HP motor, you need a 10HP VFD. Do not attempt to use one large VFD if you have separate motors that need to come on and off independently, you will kill the VFD in short order (similar issue as a single Static Phase Adder by the way).
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
------------------------------------------------------------------------
If it is broken, fix it. If it isn't broken, I'll soon fix that.
RE: How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
The tractor driven generator also seems a good option. Will this set-up be efficient, if not cheaper?
Just for specifics, the components of the dryer are: 20HP hot air blower, 3HP cool air blower, 4HP grain agitator, 1.5HP feed regulator and a 1HP screw conveyor. All run on 440V, 3-ph source and the dryer uses kerosene or diesel fuel.
Thanks for all the feedback guys, I'm exploring all options you've given me.
RE: How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?
The use of an engine is not very efficient if you count the btu content of the fuel and the power you get out of the generator, but in your situation, you should be able to route the heat from the radiator and the exhaust from the diesel into the the air stream for the dryer and capture the "waste" heat (greater than 50% of the BTU contained in the fuel) which is normally lost.
It would just take some creative thinking about how to route the cool intake air through the generator enclosure first and then across the engine and then out the radiator (pusher fan is pretty standard on generator sets) and into the intake of the dryer. I don't know if you can stand the exhaust in there (routed in after the radiator and the fan motor)because of soot particles, but since it burns diesel as the main source of heat, probably you could work it out.
RE: How to operate a 3-ph, 440V equipment using 1-ph, 230V supply?