Pipe bollard dynamics
I have this pipe bollard that is rated and crash tested per ASTM F2656 as M50 / P1. What that means is that a medium duty truck (15,000 lbs.) running at 50MPH upon impact with the bollard, stopped no more than 3.3ft. beyond the bollard line. Per the reference ASTM standard above, this would have produced a kinetic energy of 1250 ft-kips. I don't have the specific information about the condition of the bollard after impact.
Here are the details of the bollard assembly. It's a 10" dia. sched. 80 steel pipe with additional ¼" thick plate welded inside (parallel to the direction of the impact) and in-filled with grout. This bollard is embedded in a 32" wide x 48" deep continuous concrete grade beam. Bollards are spaced at 48" o.c. but only one bollard is impacted in the testing.
I'm trying to replicate the results of the testing by running the numbers. Looking at the steel bollard capacity (ignoring the grout in-fill for now – I don't think that the grout adds a significant number to the overall strength of the bollard). The bollard is not even close to taking the full amount of force generated by the 15,000lbs. truck at 50MPH.
This got me thinking about the force dynamics involved. The bollard isn't really taking the full energy of the truck upon impact. I'm assuming that some were lost due to friction resistance of the tires against the pavement. The grout inside the pipe also takes some of the energy. Also, there is an instantaneous transfer of energy occurring from the bollard to concrete grade beam then to the soil at the moment of impact while the bollard is yielding.
Are these assumptions valid? Other assumptions I might have missed? Anyone here has any experience designing bollards per ASTM F2656 or SD-STD-02.01?
Also, how do you quantify each assumption? I do have a vague idea but would like to find out what your thoughts are. I've seen some discussions here about bollards but have not found the definitive answers to what I'm looking for.
Sorry for the long post and thanks for anything that you can add to this discussion.
RE: Pipe bollard dynamics
I would assume that the bollard would be taking most of the energy - the friction of the tyres over the stopping distance would be negligible, and energy is only transferred into the soil if deformation occurs??
The force applied to the bollard can be calculated by dividing the KE before impact by the stopping distance. So you would get 378.8 kips on the bollard. I guess you could look at the plastic modulus and use a bending moment at the base of the bollard to see if it can handle this??
That's all i have at the moment!
I'll be interested to hear anyone else's input..
I have now seen a couple of videos of the crash testing and the bollard didn't even bend upon impact of the truck. It sliced thru the center of the truck and the front of truck (what's left of it anyway) protrudes a certain distance from the bollard.
You would think that the bollard would get sheared off or bent down, but that is not the case.
DaveAtkins
The truck is much softer than the bollard.
See attached article for a discussion of energy-based design method.
Based on that article, it confirms that the bollard is subjected to 378.8 kips of force as demayeng noted. What I'm having a hard time grasping is that the calculated theoretical bollard capacity, using the listed yield and tensile strengths of the pipe (A53 type E) is nowhere near the 378.8kips.
The only unaccounted element is the grout in-fill inside the pipe. Am I to believe that the grout will make up the difference or the pipe's actual strength is way more than what is listed?
The force required to create this deformation is the same as the equal and opposite force applied to the bollard.
I guess the grout fill is completely confined, meaning it would have high strength. It would also aid to prevent the pipe from buckling. So the grout-filled pipe could act as a very efficient composite steel-concrete column
This paper says they got an increase in bending strength of 25% by concrete filling:
h
Not enough to explain our situation though..
What I'm actually trying to do is attempting to correlate the crash testing behavior against the generally accepted scientific formula for determining the theoretical strength or capacity of the bollard and it's not even close. Why the wide discrepancy? That is the question that I'm trying to solve.
I was told, early in my career that this is what has been found to work in practice, don't question it.
Michael.
Timing has a lot to do with the outcome of a rain dance.
As to the truck travel- does it mean the truck never goes past that point, or rebounds to less than that point?
The spring energies of the bollard and the footing/soil that JStephen refers to must act (a lot!) to reduce the overall force experienced by the bollard. The bollard might not be too hard to work out, but the footing..