One of my friend asked me this question where he was wondering if a separate earthing design is done for isolators 220kV. These grounding/earthing are then connected to main grid. If it is done what practices are followed? He was calling this earthing as auxiliary grounding/ earthing.

If anyone practiced this kindly help

RE: Auxiliary grounding/ earthing for Isolators in substation.

Normally the operating handle has an earth mat buried beneath where the operator would stand. Is that what you mean?
Regards
Marmite  

RE: Auxiliary grounding/ earthing for Isolators in substation.

(OP)
Yes it is the one where operator will stand. He is telling me that normally he saw following for grounding/earthing

Normally For 400kV Switch Yard- Mesh Formed is LxW :: 1500mmX 1500mm spacing of rod @300mm this was beneath the isolator
 
Normally For 220kV Switch Yard Mesh Formed is LxW :: 1200mmX 1200mm spacing of rod @300mm which is beneath the isolator

If it is OK then what codes they might have followed?
 

RE: Auxiliary grounding/ earthing for Isolators in substation.

There are no codes/standards in the USA that address the size of the grounding platform.  I don't know about IEC.  I see no reason for the size of the platform to be voltage dependent.  It need to be big enough to stand on comfortably to operate the switch.  A 400 kV switch operating handle is no larger than a 220 kV switch operating handle.

 

RE: Auxiliary grounding/ earthing for Isolators in substation.

We also use a 1200mm x 1200 underground mesh for 115 and 230 kV switches.  

The operators do more than just stand winky smile Staying strictly on that size can be hard if the switch isn't well maintained or if it is ice covered.   

RE: Auxiliary grounding/ earthing for Isolators in substation.

(OP)
Any idea from where this size 1200x1200 with conductor spacing 300 came from? OR it is just a practice everybody following up?   

RE: Auxiliary grounding/ earthing for Isolators in substation.

Having additonal conductors buried beneath the finished grade will help reduce step potential for the operator, but do nothing to reduce the voltage difference due to ohmic resistance of the grounding lead between the connection to the switch handle and where the operator stands.

I prefer to install a galvanized steel platform which rests on top of the finished grade and which is bonded not directly to the ground grid, but instead to the point where the ground grid connects to the switch lever ground strap.  This ensures that the operators hands and feet are tied to the same electrical potential and can no longer be part of a shunt path.

RE: Auxiliary grounding/ earthing for Isolators in substation.

(OP)
I add all into following....please check

1. Auxiliary ground Grid should be bonded to Ground Grid where Grid connects the switch lever ground strap.

2. The purpose of this auxiliary ground is to keep potential of handle lever and ground at persons atep at same level.

3. Size 1200mmx 1200mm with 300 mm horizontal conductor spacing is just a standard practice and as it is connected to main grounding its size and conductor spacing normally dosen't vary with soil resistivities.

4. Also Size 1500mmx 1500mm with 300 mm horizontal conductor spacing is used at many places to take care of safe working space around equipment.

Please correct me if I am wrong in analysis anywhere.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources