Underground cable installation crossing existing underground cable

Underground cable installation crossing existing underground cable

Underground cable installation crossing existing underground cable

(OP)
Hello everyone, I'm currently working on a project where the new underground cable route will be crossing an existing undergound cable route at various locations. The existing and new underground cable systems are both 34.5 kV. The idea is that the new cables need to be sized and spaced accordingly such that they don't cause any derating in the existing cables due to heating effects. I'm taking a look at the Neher-McGrath method but it seems to deal more with derating of cables based on one system. Anyone has any information/references I can look at on derating of cables based on systems that cross or are in near proximity of each other? Not having much luck with search online.

Thank you  

RE: Underground cable installation crossing existing underground cable

If they are crossing at right angles, you don't have to worry much about derating.  

The Neher McGrath is applicable - heat is heat.  It doesn't matter what the source of the power is.  

 

David Castor
www.cvoes.com

RE: Underground cable installation crossing existing underground cable

There was a paper by Dorison at JICABLE in 2003 http://www.see.asso.fr/jicable/2003/pdf/A94.pdf
which was developed into IEC 60287-3-3.
There are rating tools such as Cyme and Crater which utilise the IEC method.
The calculations for crossing cables are very complicated. To get a conservative result assume that the cables are side by side, or better still increase the separation until they are thermally independent. That will also have the added benefit of improved security of supply.
Regards
Marmite

RE: Underground cable installation crossing existing underground cable

The guys at Cyme can run the case for you. Its cheaper than buying the toll/software and learning how to use it!

Desrod

RE: Underground cable installation crossing existing underground cable

Ignoring the heat from any crossing is a mistake. Heat and EMF are not the same and cannot be treated the same way.  Good information here  http://www.neher-mcgrath.com. The crossing calculation is even more complex than the normal neher-mcgrath calculation but there are several software packages that can handle it.  

Ohm's it not just a good idea, Its the law.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources