Overhead Earth Wires

Overhead Earth Wires

Overhead Earth Wires

(OP)
Is there a formula which calculates the relative proportions of earth fault return current through:
1) an overhead earth wire strung on the same poles as the faulted line; and
2) the body of the earth.
I have seen results for item 1) which include one component of earth fault current in the earth wire flowing back towards the substation and a smaller component flowing outwards away from the substation.  

RE: Overhead Earth Wires

See IEEE Std 80-2000 Section 15.9.  There several methods presented, none of which use a simple formula.  Also, commercial grounding programs such as WinIGS and SES CDEGS use more complicated approaches.

Some of the current will also return in earth wires not on the same poles as the faulted line, such as outgoing distribution feeders.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources