Cylinder variances
Cylinder variances
We have had some breaks that have come up short on their compressive strength. Problem is, is that the GC is saying we broke those cylinder 22 hours too early. I know that the ASTM gives you +/- 20 hours, but I was wondering what the variance is for AASHTO?
RE: Cylinder variances
Is this for removal of forms or supports on a time sensitive project with penalties or bonuses for the GC depending on the completion date? - This can be a major factor in attitudes and interests. I have a friend involved in a project where the contractor and supplier jointly set a control on the strength 25% over project specs to allow reliable, quick construction in harsh weather on a bridge and early completion date bonus was over $50,000,000.
Was the time of preparation of cylinders documented before testing?
The first 24 hours of curing and any handling can easily skew the results in the short term.
The technician making the cylinders can easily boost or lower the cylinder strength, especially in the short term.
Does the concrete supplier have any opinion? He would rely on the lab's value more than the short term business from one job since the GC may not be around especially if they quibble about 2 hours. - The concrete supplier should be notified in some way. I would imagine the mix design included some testing for acceptance, so this could be a reference.
Dick
Engineer and international traveler interested in construction techniques, problems and proper design.
was it short on the design strength or on the aci acceptance criteria? what would the trendline show? why not hurry up and core it? i mention that because it'll come up so you'd be better off suggesting it...BUT keep in mind the compressive strength results between cylinders and cores are NOT the same. the argument is almost impossible to win with an owner so just play the card first acknowledging that they're different and that the strength may come up. if it does, then the structural can hang his/her hat on it and the owner is happy. if it doesn't, then a more in-depth assessment can take place at the direction of the EOR or owner...or tear it out.
As for the 22 hours....I agree with msucog...no effect at all, but any deviation from a standard will bring all your results into question.
If you plot a strength gain curve, you'll see that after about 7 days, the curve flattens significantly. From 14 to 28 days, the curve is very shallow. This is the portion that will prove your point...If only 20 percent of the strength is gained between 14 and 28 days (336 hours), then for each percent of strength gain, it takes almost 17 hours. So your 22 hours might change the results by a little over 1 percent. So for a 3000 psi mix that would be a little over 30 psi...not a big deal.