Concrete column saw cut spiral reinforcing

Concrete column saw cut spiral reinforcing

(OP)
Hopefully this is the correct forum...

I have a demo contractor that was to cut away a concrete beam framed into a round concrete column.  The building is about 80 years old.  A demo saw was used and the angle was wrong, they cut through the spiral tie reinforcing, about 40" of vertical length or 13 passes of the spiral.  The spiral looks to be 3/8" smooth bar, spaced about 3".

Has anyone successfully repaired something like this?  How would you go about it?  We've considered chipping away to expose enough to re-weld all the bars, although I'm not sure of the weldability of this metal.  The other idea was to patch the concrete and wrap the column with steel plates or even FRP.  

Thanks,
Jeremy

RE: Concrete column saw cut spiral reinforcing

The circular steel plates or FRP wrap would be the best option.

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

RE: Concrete column saw cut spiral reinforcing

agree

RE: Concrete column saw cut spiral reinforcing

What is going to replace the beam at this level? If this section is going to be inside a slab then it will be adequately restrained in the final condition. Could be a temporary issue though.

RE: Concrete column saw cut spiral reinforcing

It is a requirement of modern concrete codes the longitudinal reinforcement of concrete columns be restrained by lateral reinforcement so they cut spirals will need to be re-instated. My opinion would be the use of externally bonded    CFRP. I am unsure whether there is any requirement to protect the CFRP for fire.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close