Regarding HV Test - Power Frequency - for Old SwitchGear

Regarding HV Test - Power Frequency - for Old SwitchGear

Regarding HV Test - Power Frequency - for Old SwitchGear

(OP)
Dear Sir/s,
I need some help.

I am going to put in service some only Switchgears Panels in action.

I need to know howmuch Voltage I have to inject for power frequency 1 Min test?

These swirchgears was ideal for 5 years as a spare in separate room, Now just I installed.

Its 3.3 KV & 11 KV and 33 KV.

I understand that I have to inject 75% or 80% of the factory test voltage but now its too Old.....So I am worried that howmuch I have to inject?

If I inject only service voltage the is it OK?

Kindly provide your valueable suggestions.

RE: Regarding HV Test - Power Frequency - for Old SwitchGear

Like with most questions regarding electrical testing, there are ANSI/IEEE standards that dictate the rules, or international standards depending on where you are and what you must conform to. Selecting a reduced test voltage due to worry over the age of the gear is not recommended. A test performed at normal operating voltage is no test.

The test voltage depends on the type of SG it is. The test should be done with AC voltage. A one minute AC power frequency withstand test is appropriate. I don't have the chart for your voltages but I am sure they are close to the standard voltage classes here (US). For the 3.3 kV it will probably be 14kVac, the level used for 4160 gear. Assuming the 15kV SG rating spec would apply to your 11kV, the test should be 27kVac and for the 33kV, it will probably be 60kVac.Check with you local standards for the exact voltage ratings of the gear you have.

Good Luck.

RE: Regarding HV Test - Power Frequency - for Old SwitchGear

(OP)
Dear Mr.VL,
Thank you verymuch for your valuable support.
I will do needful accordingly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources