Transformer Tertiary is not loaded, why its winding temperature higher

Transformer Tertiary is not loaded, why its winding temperature higher

Transformer Tertiary is not loaded, why its winding temperature higher

(OP)
THe tertiary is not connected to the load, but its winding temperature gauge reading is highest among the three windings.

I would like to listen to your opinion.

RE: Transformer Tertiary is not loaded, why its winding temperature higher

check the calibration of temp gauges
 

RE: Transformer Tertiary is not loaded, why its winding temperature higher

More details required. Voltage ratio,rating, winding configuration, transformer purpose, unbalanced loading, harmonics etc.
Regards
Marmite

RE: Transformer Tertiary is not loaded, why its winding temperature higher

What are the temp readings? plus other info requested by Marmite.  There is no useful information in your post.

Rafiq Bulsara
http://www.srengineersct.com

RE: Transformer Tertiary is not loaded, why its winding temperature higher

zero sequence currents?

RE: Transformer Tertiary is not loaded, why its winding temperature higher

(OP)
My point is that the winding temperature reading is the simulated value.  Basically it's the oil temperature plus the diverted load current times a constant that was pre-calibrated by the OEM.

My question was, if there is the zero load current in the tertiary (tertiary is not connected to the load), how the tertiary winding temperature was higher than the other two winding?  the winding temperature of tertiary should not exceed the oild temperature.

RE: Transformer Tertiary is not loaded, why its winding temperature higher

Probably need to talk to the manufacturer.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: Transformer Tertiary is not loaded, why its winding temperature higher

is the ct feeding the gauge from the correct winding?  It could be that you have a ct from HV or LV wired to the TV gauge.

RE: Transformer Tertiary is not loaded, why its winding temperature higher

If the tertiary is delta, unbalanced primary voltages may cause heavy circulating current in the delta.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Transformer Tertiary is not loaded, why its winding temperature higher

Imbalanced loads will overheat the tertiary.  We once made the mistake of single phasing a 40 MVA transformer line to line at just a few MVA and smelled burned oil within minutes.  The tertiary wasn't connected, but it sure burned up nice.   

------------------------------------------------------------------------
If it is broken, fix it.  If it isn't broken, I'll soon fix that.

RE: Transformer Tertiary is not loaded, why its winding temperature higher

(OP)
"Unbalanced Load" - Excellent Point, thanks!

RE: Transformer Tertiary is not loaded, why its winding temperature higher

How large is the temperature difference?  I have measured adjacent probe pockets with a difference of several degrees C.

Is the CT feeding the gauge on the tertiary bushings, or on the delta part of the winding?  If they are on the bushings you have a calibration problem.

Are they separate gauges or an electronic monitor?

RE: Transformer Tertiary is not loaded, why its winding temperature higher

The tert windings are still connected to each other - ie: not open circuited.  This acts like a shunt for unbalanced currents and is one of the main functions of a tert winding.  Unless you are exceed temp limitation everything is probably fine.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources