460V to 400V AC 3PH
460V to 400V AC 3PH
460V to 400V AC 3PH
I have a bunch of european equipment that runs on 400VAC 3PH.  Currently, we are stepping 460V down to 230V with one transformer.  Then going from 230 to 400 with another.  This seems like such a waste of resources just to drop the voltage 60 volts.  There has to be a solution out there besides custom built transformers.  Anyone solve this problem?
RE: 460V to 400V AC 3PH
If voltage is your only issue (I would imagine that frequency is too), then you need what is called a "buck boost" transformer. Easy to order, easy to install, available in a wide variety of voltage reductions / gains.
But what are you running? AC motors may not need any changing at all, and in fact if you do drop the voltage you may burn them up. Post more details.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
It is machinery from France that requires 400 VAC 3PH,  50 or 60 Hz.  The power is distributed to Servo, AC drives, and 24VDC power supplies in the machine panel.  I've looked at many different buck/boost transformers, but can't seem to find one that "bucks" 60 volts.
Ask your local electrical rep (Sq D, GE, ABB or the like) to quote an auto-transformer, which is what a buck-boost transformer is. Provide them the ratings you want.  Even look up and ask any transformer manufacturer in your area.
The term buck-boost is generally associated with smaller sizes auto transformers (a few VA and 240 to 220V ), in the USA.
Rafiq Bulsara
http://www.srengineersct.com
If you don't need a neutral the open delta auto transformer is often the cheapest solution.
Bill
"Why not the best?"
Jimmy Carter