Does reinforcing area used for Shear Friction according to ACI 318 section 11.7 count towards the maximum steel percentage for 0.75pb?

RE: Shear Friction Reinforcement VS. Max Steel Area

You can count for longitudinal steel to account for Shear friction. As long as there is no net tension on the section, the longitudinal steel that is used for flexure can also be used for shear friction.

See commentary for 11.7.7 (ACI 318-05)

Quote:


When moment acts on a shear plane, the flexural tension stresses and flexural compression stresses are in equilibrium. There is no change in the resultant compression Avf fy acting across the shear plane and the shear-transfer strength is not changed. It is therefore not necessary to provide additional reinforcement to resist the flexural tension stresses, unless the required flexural tension reinforcement exceeds the amount of shear-transfer reinforcement provided in the flexural tension zone. This has been demonstrated experimentally.

RE: Shear Friction Reinforcement VS. Max Steel Area

(OP)
So if I have a bending moment around a corner of a wall that req's As = 0.31 sq.in. of steel, and the shear values exceed the allowable Vc and I need to use Shear Friction, do I not have to "add" additional steel?  If Avf = Vu/(phi*Fy*mu) = 0.09, do I not have to use 0.40 sq.in of reinforcing?

RE: Shear Friction Reinforcement VS. Max Steel Area

blawson,
Can you expand a bit on your wall corner example?  Usually the reinforcement used for bending is orthogonal to the shear reinforcement in a bending member since the shear cracks are usually at an inclined angle to the flexural "beam" and thus the shear reinforcement is not aligned with the flexural.  Thus there is no conflict.

 

RE: Shear Friction Reinforcement VS. Max Steel Area

Shear reinforcement for out of plane bending in walls is not a common thing, and normally indicates the walls are too thin.

RE: Shear Friction Reinforcement VS. Max Steel Area

You can't use shear friction reinforcement to make up for a deficiency in shear capacity of the concrete.  As JAE mentioned, you use stirrups for that.

But I wouldn't use stirrups in a wall--I would thicken the wall as hokie66 suggested.

DaveAtkins

RE: Shear Friction Reinforcement VS. Max Steel Area

Just to point this out, too.  You can only use shear friction
in certain circumstances. You need to have a
cold joint or a reasonable expectation that a crack will occur along the plane in question - a SHEAR plane.  Diagonal tension cracking doesn't count as a shear plane.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources