Good day to all,
Recently I had visited a power plant abroad USA to survey winding conditions for 8.1MW 13.8KV
During my inspection noticed that generator's power cables are not grounded at generator's junction box.
Power cables are only grounded ay substation switch board!
Will someone please revert if this is correct?
So far I have never witness medium voltage power cables connecting the generator and MSB, to have only one end grounded

Kind regards
ermioni   

RE: 13.8KV Generators cable termination

So you are saying the cables that run from the generator junction box to a remote switchboard are grounded only at one the remote switchboard end?

I agree that is not correct.   There should be stress cone at both ends with shield of stress cone connected to ground.  
 

=====================================
(2B)+(2B)'  ?

RE: 13.8KV Generators cable termination

(OP)
Dear electripete,
Much appreciated your prompt feed back,
the answer is YES only on site is grounded on the power cables and that is at Main Sitch board, but not generator site,
will it be possible to elaborate bit details so I can revert to the client,
also see attached photos with damaged end boot terminations
Sincerely
ermioni

RE: 13.8KV Generators cable termination

Details... you mean like a reference?  I don't have one handy but I can look later if no-one else comes up with one.

The photo you attached was  the generator lead (not the cable from generator to remote panel), right?   Was there a question about the photo?
 

=====================================
(2B)+(2B)'  ?

RE: 13.8KV Generators cable termination

(OP)
Hi electripete,
these are the single contactor cables from generator's junction box to main switch board.
One conductor per phase!
Thank you

RE: 13.8KV Generators cable termination

So there is no stress cone at the termination of the shield? That would be a problem.

=====================================
(2B)+(2B)'  ?

RE: 13.8KV Generators cable termination

I'm assuming what you're showing is a shielded cable with no stress cone at the termination.

The stress cone has a purpose – to reduce stress concentration which would otherwise occur at abrupt interruption of the shield.   Without it, I guess this is what you get.

Here is a reference:

Quote (NEC):

300.40 Insulation Shielding
Metallic and semiconducting insulation shielding components of shielded cables shall be removed for a distance dependent on the circuit voltage and insulation. Stress reduction
means shall be provided at all terminations of factory applied shielding.

=====================================
(2B)+(2B)'  ?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources