Disconnect for Air Cooled Chiller

Disconnect for Air Cooled Chiller

Disconnect for Air Cooled Chiller

(OP)
I have (3) 500 ton air cooled york chiller units going in that have single point connections. The chiller package has 4 compressor units (2 units from 2 control sections)with . Both control sections are contained within a single control cabinet and have their own molded case breaker capable of being locked out and operated externally while the control panel is closed. The single point connection within the cabinet shows our single point feed cables landing on a terminal block and from the terminal block are wired to each of the (2) breakers. All controls are downstream of the breakers.

Is there any reason to provide a single point disconnect? I realize it would be better practice but this is a temporary installation and it would be nice to eliminate the cost of (3) Nema 4X 1000A disconnects.

RE: Disconnect for Air Cooled Chiller

I don't know of any code requirement for a single disconnect.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: Disconnect for Air Cooled Chiller

Agree with Alan -- if the first thing your cables hit are the line side of 2 circuit breakers, the breakers should suffice as disconnecting means.

Good on ya,

Goober Dave

RE: Disconnect for Air Cooled Chiller

I think you can label the equipment to indicate that both breakers must be opened for disconnection. Check with the AHJ.

RE: Disconnect for Air Cooled Chiller

Is there any disconnect for the motor?  Or do those breakers only disconnect the controls?  If not, you will need an additional local disconnect per 430.102 unless you fall under one of the exceptions to 430.102.  That disconnect would most likely be placed just ahead of your single-point connection.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources