gpm thru plate heat exchanger
Im looking for the calculation for finding gpm thru a plate heat exchanger for a 30 ton chiller
RE: gpm thru plate heat exchanger
Q=m*C*(T1-T2)?
You must be able to tell us more than that.
There are a lot of basic design parameters that you have to specify, i.e., what is the design delta T for the coolant, what is the design ambient?
As an example, based on a system we designed for a smaller military application with a 5°C delta T and 400 W load, the scaled coolant flow would be 264 gpm, but that probably has little correlation with your system
TTFN
Depends on PHE design (size, corrugation, plates, ...) Get manufacturer´s calculation programs like here:
www.kelpie.se
Call the manufacturer with the pressure drops across it. He'll be able to tell you within a few minutes exactly what the flow is.