Hi,

I need to hook up 138kV, 1ph ssvt (inductive type) to a bus via fuse link disconnect. The maximum SLG fault current at that bus can be 20kA (symmetrical) from my study. But, the maximum fuse rating available in the market is only 12.5kA (symmetrical). Can I still use this fuse to protect the SSVT. The insulator and the remaining structure can withstand 20kA for sometime.

I learn that typically the 138kv ssvt units are hard bus connected without any fuse or disconnect switch. Considering that, I thought what I propose is definitely a better solution if not better.

Will a fast acting fuse serves better than normal speed fuse? After all this fuse is meant to blow anything more than 5 amp current

RE: Fuse Rating for Short Circuit

No. Probably better to do without than have an under-rated fuse.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: Fuse Rating for Short Circuit

(OP)
Alehman, Can you explain why? I may be missing some basics here :(

RE: Fuse Rating for Short Circuit

If the fuse is over rated there is no guarantee that it will interrupt the fault current at all and in attempting to do so it may fail disruptively or catastrophically.
Regards
Marmite

RE: Fuse Rating for Short Circuit

(OP)

Marmite - In this case the fuse is actually underrated for short circuit fault. Its never meant for overcurrent.

Available short circuit at the bus - 20kA
Fuse capability - 12.5kA

RE: Fuse Rating for Short Circuit

What Alan said. Marmite probably meant over "dutied" (or underrated).

The fuse SCC rating has to be equal or greater than the available max. fault current, which is 20kA in this case.

Rafiq Bulsara
http://www.srengineersct.com

RE: Fuse Rating for Short Circuit

(OP)
Thanks Rafiq. I agree that engineering design and perhaps code also does not allow for underrated fuse.

I thought the fuse will anyways blows off much less than 12.5kA...

RE: Fuse Rating for Short Circuit

Rafiq,

So you are saying the fuse should blow just fine, except it may not be able to interrupt the current during a fault (since it is rated well below the availble fault current)?   

RE: Fuse Rating for Short Circuit

(OP)
But in any case I am still trying to understand the consequences of installing underrated fuse?

Sure, I will not recommend it smile

RE: Fuse Rating for Short Circuit

Quote:

consequences of installing underrated fuse

What Marmite said...., politely.  

Rafiq Bulsara
http://www.srengineersct.com

RE: Fuse Rating for Short Circuit

Even if the fuse were adequately rated, the bus protection would trip anyway for a VT fault.  The only advantage of the fuse would be that you would know where the fault was.  Chances are, with or without a fuse, the VT would be smoke anyway and obviously the source of the fault because only a VT failure would blow the fuse.
 

RE: Fuse Rating for Short Circuit

(OP)

Depends on how sensitive the 138kV differential is set to trip. The SSVT is only 100kVA @ 138kV = 0.73Amps. That's too small a current for differential to pick - up.  

RE: Fuse Rating for Short Circuit

Rammie, what makes you think that the fault current would be limited to 0.73A, and hence not trip the busbar protection? I don't follow the logic.
Regards
Marmite

RE: Fuse Rating for Short Circuit

Things that could happen from an over-dutied fuse, include that it will launch the ends of the fuse cartridge at great speed, or it might initiate an arc that then jumps to  ground or other phase. These are catastrophic failures that can burn buildings down and/or kill people.  

RE: Fuse Rating for Short Circuit

(OP)

Marmite - I agree that the fault current will be more than 0.73Amps. I take back my statement, I gotta get back to my basics. Thanks for the correction!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources