Steel deck roof diaphragm plus sheathing
My current project has two buildings that are apparently required to be 'non-combustible' and as such have CMU walls, l.g. steel roof trusses and metal roof deck. The architect wants asphalt shingles which require 3/4" sheathing for a nailing surface.
I'm comfortable designing for lateral forces assuming the wood sheathing is my diaphragm. However, I am not sure how to fasten the sheathing through the decking to ensure diaphragm action, let alone what to use for the decking as its only purpose here is to shield the sheathing from fire.
This, in my opinion, could be easily accomplished by 2 layers of sheetrock on the roof truss bottom chords or cement board, but the architect says it is required.
The questions are:
1. How should the sheathing be fastened? (I'd like to emulate typical 6"oc/12"oc with self tapping screws, but that would seem quite a bit more labor intensive than using 16d nails driven pneumatically).
2. Can the steel deck serve as the diaphragm? I assume it can, but where can shear values be obtained for this? Obviously they are not in the NDS.
3. If it is easier to use the sheathing as the diaphragm as it is required anyway, what should be required for the deck if it is simply serving a purpose of non-combustibility?
The questions are:
RE: Steel deck roof diaphragm plus sheathing
EDIT: 16d nails obviously not necessary for sheathing.
From a cost perspective, I have been told that it is often more expensive to provide FRT plywood instead of sheathing over metal deck.
Another cause for concern with FRT plywood is the corrosive nature of the FRT chemicals. I really don't like the idea of placing a material of this nature against the light gauge truss material.
Nick Deal, P.E.
Michael Brady Inc.
http://www.michaelbradyinc.com
He sent me some helpful links with allowable shears for different products.
Based on my loads and 2'oc truss spacing I'm fine with a 1.5" 24g deck with #10's at every rib. I could probably go every second rib, but I'm not going to.
Then 5/8" OSB with 2" #6's at 12" o.c.
I think you are on the right track. I would prefer to use 22g deck and increase the truss spacing to five or six feet.
BA
Nick Deal, P.E.
Michael Brady Inc.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
I was just curious how yins handle a diaphragm on a sloped/gable roof since the sheathing is discontinuous in the middle and how the shears are transferred to the end walls.
BA
For load transfer at the side walls, I use sway blocking/panels to transfer forces at the truss heels to the supporting wall below. For gable end walls , I either run the sheathing up the face of the gable truss or specify a drag truss (designed for in-plane shear) if it occurs along an internal shear wall.
Nick Deal, P.E.
Michael Brady Inc.
Just pickin' brains here, I don't get involved in this kind of design and would like to know more.
Amazing, you answered me prior to my post.
You're like my wife....
BA
Mike McCann
MMC Engineering
Motto: KISS
Do you need a cold one or something?
I'm just relaxing and codgitating prior to addressing a contractual difference with a client. The drink(s) will come later. (smile)
Mike McCann
MMC Engineering
Motto: KISS
I think shear transfer trusses are required wherever the diaphragm is responsible for transfering lateral loads to shear walls, right?
I require blocking at heals.
I had never considered the issue of discontinuous sheathing at the ridge. Thanks for bringing that up.
I'm not familiar with the heel blocking details or Shear transfer trusses.
I marked it "Revise and Resubmit" and noted that the trusses had to act as part of the LFRS.
I got a call from the fabricator and he educated me that he could easily accommodate this, and on smaller buildings the design may not even change, but that it had to be noted on drawings (it was in the spec anyway). I think that designing trusses for transfer of in-plane forces is pretty standard. Out-of-plane is another story and is more complicated as it must be achieved with bracing.
In terms of heel blocking - a lot of builders use 2x blocking cut to the truss/rafter spacing (minus .75") because it makes layout really easy as they are setting trusses.
Codgitating? I assume that is deep thinking by old codgers.
Yes, we used to use blocking on trusses with taller heels (when I worked as a nail bender) only up to the point where they didn't suffocate the soffit/ridge vents.
I also never cared for "gable" trusses that only had vertical web members.
To avoid using them, I simply used regular trusses at the ends but set them back the wall thickness and balloon framed the gable end wall.
Then, the last truss nailed directly to the wall studs and also served as a drywall nailer.
I hated the gable trusses because they made the gable sheathing very wavy and screwed the siding up.