Looping a power supply through a circuit breaker twice.
I have got a control design and notice that the single phase power supply went through a three phase circuit breaker twice. I have asked our electrical engineer here, but he told me there was a reason for it but he cannot remember what the reason is. Can anybody here tell me what the reason is?
I have attached a copy of the design drawing and marked the circuit breaker.
RE: Looping a power supply through a circuit breaker twice.
Circuit breaker arc suppression is more of a challenge with DC since there are no zero crossings to assist in killing the arc.
You'll find the practice documented in the specs of some breakers with interrupt ratings listed for single pass and multiple pass through the breaker. We use MCB breakers spec'd and UL listed for this as the shunt trip for 48 volt DC plants as the EPO.
One would presume that the instantaneous interrupt requirements for your circuit similarly requires..
Pull the spec for the C/B and see if the 2 pass configuration is listed and supported by the manufacturer.
(Similar wiring is used in DC circuits for entirely a different reason, to provide multiple breaks.)
Rafiq Bulsara
http://www.srengineersct.com
When differential trip is a feature see Rafiq's comment.
Many O/Ls intended for motor protection have a differential feature and all three poles MUST be used. The loop back is common when single phase motors are fed from a three phase motor protection device.
Bill
"Why not the best?"
Jimmy Carter
David Castor
www.cvoes.com
As is the case with "circuit breakers". Here in North America, what we call a low voltage "circuit breaker" is a UL489 listed device and in that design, looping through is unnecessary because they do NOT have differential trips that would bias the trip threshold if current were not passing through all 3 legs. As Bill said it is OK and maybe even preferrable if you have a 3 pole device, but not absolutely necessary.
But in IEC countries, the term "circuit breaker" also includes devices that we can only call "manual motor protectors" because they have adjustable thermal trips (something precluded on UL489 non-solid state "circuit breakers"). Most of those are only available as 3 pole devices and because they are more often used for motors, also include the differential trip feature. Given the very low current trip rating shown in your drawing and the range, indicating adjustability, that appears to be the type of "circuit breaker" you are using here. So it is absolutely necessary to have current pass through all 3 poles on that type of device.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies