TYPE - B Gas Vent for Oil Fired Boilers?
Hello Everyone,
I have a design where we're installing (2) 200 HP steam boilers. The steam boilers are gas and oil fired.
We plan to route (2) 18" vent stacks(each boiler has 18" vent stack connection) into (1) 28" common vent straight up and out through the roof.
I'm looking at a UL rated, type B venting system for the vent stacks. I know it's ok for a gas-fired boiler, but is
a UL rated, type B venting system OK for oil-fired boilers?? They'll use gas most of the time, but they could use oil in the event of an emergency.
Other than the IMC 2006, is there another reference source that I need to check to see if oil-fired boilers can be connected to the type B venting system?
Thank for any info that someone may give.
RE: TYPE - B Gas Vent for Oil Fired Boilers?
AirJet "L" Vent is listed for use with modern high-effi ciency oil or gas fired appliances with operating flue temperatures up to 570° F. Type "L" Vent is designed for appliances requiring negative or neutral pressure venting systems.
• Appliances which meet the above requirements are suitable for use with Type "L" Vent. These
include oil fired furnaces, boilers, water heaters, room heaters, and decorative appliances. In
addition, gas fired Category I equipment or equipment listed as suitable for use with Type "B" Vent
may be vented with Type "L" Vent. Installation is in accordance with applicable standards NFPA
31, NFPA 54, and NFPA 211.
For more info go here: http://www.continentalindustries.com/files/downloads/AJ-LVent-Install.pdf
In my area, Type B vent is for natural gas only.  Solid fuel appliances as well as oil appliances require Typa A venting.
Are the boilers power burners?  If so, you should ensure combination venting is approved for the burners.