Use of girder distribution factor in EXTREME EVENT II
I'm designing a connection for a guide rail post to a fascia beam. I'm using design criteria from AASHTO LRFD Bridge Design Specs. A13.2. I have the load combinations as 1.25(DC2)+0.5(LL_IM)+1.0(CT) as per table 3.4.1-1.
The question is would I add in the girder distribution factor to the LL_IM. I would think not but not 100% sure.
Please post your thoughts, comments. Thanks.
RE: Use of girder distribution factor in EXTREME EVENT II
You use the forces in Table A13.2-1 for the required Test Level.In NY the TL is a function of the road type and traffic volume.
Right. The CT (transverse load)is 54 kips for TL-3 from that table. Are you saying just the 54 kips is applied with no load combinations? I thought in the beginning of section A13 it says extreme limit state applies and EXII seems to be the best choice.
But to answer my own question I would add the GDF into the LL_IM part of the load combination. It dawned on me during the ride home.
Let me know what you think. Thanks.
The connection of the post to the stringer is based on the collision force only. Your load factor for CT = 1 per Table 3.4.1.-1