Can someone tell me what the sight glass is actually used for in HVAC DX cooling refrigeration piping? Thanks.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Sight Glass Use in Refrigeration Piping
|
RE: Sight Glass Use in Refrigeration Piping
RE: Sight Glass Use in Refrigeration Piping
There's never any sub-cooling in a receiver. You've got gas on top and liquid on the bottom. By definition you have a saturated condition in a receiver.
RE: Sight Glass Use in Refrigeration Piping
Never say never but for the most part you are correct if the receiver is in a hot ambient, sub-cooling may be lost as refrigerant sits in the receiver. This is why some commercial systems have receiver bypasses for certain situations. Receiver bypasses are nothing more than a liquid line solenoid valve controlled by a thermostat, which will bypass liquid around the receiver to the liquid line.
RE: Sight Glass Use in Refrigeration Piping
When a system is operating, subcooled liquid enters and exits the receiver quicker than the pressure and temperature can achieve an equilibrium. The liquid/vapour interface is the only location where saturated conditions exist. This is why when you measure the outlet temperature of a receiver it is almost always subcooled; in reality, most of the receiver is full of subcooled liquid if the unit is operating properly. Some systems do bypass liquid to gain some efficiency, particularly if they have mechanical subcooling.
As imok2 said, a sightglass is used to determine whether a solid column of liquid is present in the liquid line. This helps in troubleshooting many problems such as refrigerant charge, lack of subcooling, plugged filter/driers... etc