Sprinkler for the HVAC SHAFT
Sprinkler for the HVAC SHAFT
(OP)
hAVE YOU EVER SEEN SPRINKLER SYSTEM PROVIDED AT THE TOP OF THE SHAFT INSTEAD OF THE VENT?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Sprinkler for the HVAC SHAFT
|
RE: Sprinkler for the HVAC SHAFT
NFPA 13 Sprinkler System
Sprinkler is provided at top of shaft, refer to exceptions, shafts with combustible surfaces require
coverage at alternate levels, accessible noncombustible shaft has sprinkler at bottom, 8.14.2.
RE: Sprinkler for the HVAC SHAFT
RE: Sprinkler for the HVAC SHAFT
Per NY CITY builidng code, title 27/subchapter 5, 27.344:
" all closed shafts have to be vented".
Now smoke vent provision is also not feasible in my case, as vents would be sticking out of the ground, and the ground will be used as the golf course.
so someone came up with instead of smoke vents provide sprinkler. which is harder as drain for the sprinkler, access to sprinkler head is a problem.
is there any reference which would allow me to go without the sprikler/smoke vents for these shafts?