tank ventilation rate

tank ventilation rate

tank ventilation rate

(OP)
I am trying to find the recommended ventilation rate for chlorine dioxide storage tank. It is necessary to keep the cl02 concentration in the vapor space below LEL, but there should be the minimum recommended rate. Does anyone come across with such a data?

RE: tank ventilation rate

sweetfood:

I would be interested to know where the vent is routed?

Milton Beychok
(Visit me at www.air-dispersion.com)
.

 

RE: tank ventilation rate

(OP)
It is routed to scrubber system where multiple vent lines are connected. I know the maximum capacity of tail gas at scrubber system but it is unrealistic to use this number for storage tank since, again, multiple lines are connected to the scrubber. There is the recommended miniminum vent rate for Cl02 tank.  I've seen it before but I can't find it any longer. I may have to calculate based on solution temperature and tank pressure to see how much of Cl02 can be found in vapor space within tank. Do you have any recommendations?

RE: tank ventilation rate

According to the msds, chlorine dioxide LEL is 10%.  In your product conveying duct design, you need to keep the exhaust below 25% of the LEL which is 2.5% in accordance with 2007 CMC 506.   

RE: tank ventilation rate

The ventilation rate equation will be a first order DE if the generation rate is constant. Refer to the first order DE in my response to thread 1043-272680; however,you'll need to reconfigure the units of SDTOBIN ppm(V) presented above to my units ie, mg/cu.m= (Molecular Weight/24.45(@25 dC))*ppm(V).  The generation rate of chlorine dioxide will be hard to determine and don't forget to have fresh air for makeup contaminated air removed.

RE: tank ventilation rate

(OP)
Thanks for your help, everyone.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources