WHM Re-calibration for changing CT ratio

WHM Re-calibration for changing CT ratio

(OP)
I am changing a MV feeder which has existing GE type DS WHM presently fed from 400/5 CTs, I am changing the CTs to 600/5. Is it sufficient to change the meter multiplier by a new multiplier 1.5 multiple (6/4) of existing multiplier or a more elobrate recalibration is required? The meter is not used for revenue metering.

RE: WHM Re-calibration for changing CT ratio

Just change the multiplier.  Since the CT wiring changed, you may want to verify that teh connections are correct.

An old electrician trick is to open the CT test switch  or insert the shorting screws at the CT terminal strip one at a time.  The meter should slow down when a phase current is cut out.  If it speeds up something is wrong.  If it slows down, it might be correct because the test does not find all errors.

RE: WHM Re-calibration for changing CT ratio

Meter multiplier is CT effective ratio (600:5A = 120:1) multiplied by the VT effective ratio (if one exists).

 

RE: WHM Re-calibration for changing CT ratio

Whilst it may work it is a very rough and ready way to do it and may well lead to confusion in the future, unless very clearly labelled and documented.  Most relatively modern meters are programmable so you should be able to connect to it and change the CT ratio and pulse multiplier (if applicable) to a suitable value.  

You do need to ensure that you do not exceed the maximum pulse rate for the meter, you will be able to find this in the meter technical data sheet.  If this rate is exceeded there won't be sufficient discrimiation between pulses and the system won't work correctly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources