I am designing a large paint booth (60'x22'x21') to be located inside a large enclosed industrial building.
  
I read an old post on this forum that suggested that the 10 PSF minimum wind pressure (IBC 2006: 6.1.4.1) is to be used for an "indoor" structure.   This seems very conservative, and I cannot find justification for it in ASCE 7 or in IBC 2006.  The old Wisconsin code required a 5 PSF wind load for interior structures, which seems more reasonable, but this provision does not appear in the new codes.  Because this structure is in Wisconsin and because it is very light, a 5 PSF wind load would be substantially larger than the seismic load.

What do you think?  What do the codes require for an "interior" structure?
 

RE: Interior Wind Loads

Check 2006 IBC Section 1607.13.  It looks like 5 psf is required unless there's something special happening (seismic, internal HVAC pressure, etc.).
It's not really a wind load, but that seems to be a logical justification.

RE: Interior Wind Loads

I might consider using the interior
portion of the MWFRS pressure.

RE: Interior Wind Loads

(OP)
Thanks guys!

RE: Interior Wind Loads

It used to be 5psf for firewalls

Michael.
Timing has a lot to do with the outcome of a rain dance.

RE: Interior Wind Loads

Since your building is "industrial" it is probably designed as "partially enclosed". Considering that, use the interior pressure as your design criteria, but as ASCE 7 notes, not less than 10 psf for any component or cladding.

RE: Interior Wind Loads

Higher than 5 psf is adviseable for bathroom enclusures.

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

RE: Interior Wind Loads

5 psf is adequate, unless the paint booth must be designed for an explosion.

The 10 psf minimum component and cladding load is for exterior walls.

DaveAtkins

RE: Interior Wind Loads

(OP)
Thanks to everyone for your help!

RE: Interior Wind Loads

It depends on the situation.  Consider a carwash facility with front and back doors, either of which could be open or closed at any given time.

With two adjacent bays, the windward door is open on one while the leeward door is open on the other.  The partition between the two units is subjected to the full positive pressure on  the windward side plus the full negative pressure on the leeward side.

In such a situation, a pressure of 5 psf or 10 psf on the interior partition would be woefully inadequate.  Such a partition may be more critical than an exterior wall.

BA

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources