I have old (40y) TG control panel with about 30 pilot lights.
About 10 of those lights are 480VAC. What i want to do is to bring all of those lights to the PLC HMI. However 480 VAC presents the problem.
Cannot modify the source of the 480VAC pilot lights.
Short of installing step down transformer on every light what are my other options? Could not find any interposing relays with 480 VAC coil.
Any feedback is appreciated.
Thank you
About 10 of those lights are 480VAC. What i want to do is to bring all of those lights to the PLC HMI. However 480 VAC presents the problem.
Cannot modify the source of the 480VAC pilot lights.
Short of installing step down transformer on every light what are my other options? Could not find any interposing relays with 480 VAC coil.
Any feedback is appreciated.
Thank you





RE: 480 VAC pilot Lights
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 480 VAC pilot Lights
David Castor
www.cvoes.com
RE: 480 VAC pilot Lights
The alternative is to use a small IEC type contactor with a 480VAC coil. Not as small as an interposing relay, but in a crunch will work.
RE: 480 VAC pilot Lights
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: 480 VAC pilot Lights
RE: 480 VAC pilot Lights
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: 480 VAC pilot Lights
Some industries are moving away from even 120 V ac control circuits and converting to 24 V dc.
David Castor
www.cvoes.com
RE: 480 VAC pilot Lights
The prints I had for this Panel date back to 1954. However, somewhere along the lines someone changed 480 VAC lights to 125 VAC.
Thank you for tips