Vane Type Water Flow Device
2

Vane Type Water Flow Device

Vane Type Water Flow Device

(OP)
Does anyone here know the distance required from a paddle type flow switch and a Elbow. I try finding such code but no luck yet.

RE: Vane Type Water Flow Device

(OP)
Oh ok. I guess this kind of information you find on the manufacturers spec sheet.

RE: Vane Type Water Flow Device

Yes.  If you can't find information in the standards, be sure to check the data sheets.  They often have the criteria.

This data sheet is also why some engineers specify no more than 18 fps in risers.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: Vane Type Water Flow Device

(OP)
The only problem with this is that is not a mandatory requirement so that means it could be ignored if the installation calls for drastic measures. For example:
If you only have 6 inches between valve and ell-bow you really have no other choice correct.

RE: Vane Type Water Flow Device

It is in the manufacturer's data sheet, so it is a requirement.  I have had to do some unique pipe routing to maintain some of these requirements.

If the data sheet stuff is not a requirement, then I guess one could install Tyco attic heads at 12" from the roof deck and have the deflector parallel to the roof as that is how NFPA 13 says a sprinkler should be installed.  However, that would be an incorrect installation and not meet the sprinkler listing requirements.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: Vane Type Water Flow Device

(OP)
Oh no absolutely. What i meant to say is that if you read the manufacturers spec you provided it indicates "SHOULD" not be installed within 6" of a fitting. That automatically changes everything. It id said "SHALL" be installed on the top side of the horizontal pipe.
You know how I feel about SHOULD vs SHALL  

RE: Vane Type Water Flow Device

It is interesting that the terminolgy changes from the 'Shall' stated in regards to the WFS being installed on top of the pipe, to using 'Should' for the clearance fro valve/fitting.
And then you have the likes of this
http://www.victaulic.com/Docs/lit/10.96.pdf
My understanding is that since the manufacture has received approval based on this arrangement that it is ok to have the WFS basically right beside the valve/drains/fittings.
To be honest seeens a bit 'bogus' that the manufacturers of these Riser Control Assemblies can get approval for the WFS close to the Valve/Drain but the WFS manufacturer can't.(?)
Posible that the term 'should' was chosen over shall to allow for these type assemeblies.(?)
Also, while having the conversation :),as you mentioned there are some projects that the Engineer can specifiy to reduce the velocity in risers to comply with the maximum allowable surge stated on the datasheet. However, since this is stated on the manufacturers datasheet, with the same theory that the manufacturers recomendations become requirement for installation, then it would seem that even if the engineer has not specified a restriction on the velocity in riser, that the restriction still exists by way of the datasheet, and therefore should be standard practice anyway. (I don't usually see this happening).
Thoughts?

RE: Vane Type Water Flow Device

(OP)
Do you see why I have a great hard time when arguments come to light. I believe that if you tell me you shall not do this based on an approved code than I have no choice to do it the other way. However you are looking at an approved device listed for the purpose.
Our first discussion had nothing to do with approved listed devices rather than field installations. If you have to install a flow device based on the original argument what would you do? Remember that the specs said should not.   

RE: Vane Type Water Flow Device

Its a water flow switch kids. Travis is correct. Why do you want it to be something special?

Let Travis produce his shop drawings.

RE: Vane Type Water Flow Device

(OP)
We are not saying Travis is not correct however the fact still remains that is this case the manufacturer is contradicting the requirement. Thats all. When I read the spec I will say "Oh well it should not be closer than 6" from a fitting but is not mandatory"
 

RE: Vane Type Water Flow Device

(OP)
I guess we can all be clear on this discussion. I just got of the phone with potter and their interpretation in that is recommended but not required since the word SHOULD is in place. I just want to make sure that my technicians do the right thing out in the field.

RE: Vane Type Water Flow Device

Good info NJ. Thank you,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources