Fire pump test header sizing

Fire pump test header sizing

Fire pump test header sizing

(OP)
NFPA 20-2007 allows the designer to hydraulically size the pipe for the test header art. 4.20.3.4(2).

There's no mention of the acceptable pressure.  Figure 4.20.3.4.(2) identifies the elements that must be included in the calculation, but there's no design critereas.

Should I consider that the acceptable pressure drop is the residual pressure of the water source at a flow of 150% the nominal pump flow?

Thanks

RE: Fire pump test header sizing


Size such that it is possible to flowtest at 150% of nominal pump flowrate.

Use minimum suction pressure possible, which is residual pressure (at pumping flowrate), at the residual hydrant tap-in, less losses between the residual hydrant and the pump suction flange.  To the minimum suction pressure, add 65% of the rated TDH (total dynamic head) of the pump.. That is the minimum discharge pressure.    

Size the test header to be able to flow 150% of pump flow with this discharge pressure you calculated.




 

RE: Fire pump test header sizing

(OP)
Thanks.

If you look at figure 4.20.3.4.(2) in NFPA 20-2010 the last line showns a minimum pitot tube pressure of 18 psig.

Does this means that the minimum pressure at the flow measuring location is 18 psig?  FM global recommends a minimum of 10 psig.

Adding all pipe length, fittings and elevation in this form, we will get a calculated pressure drop at 150% pump's nomial flow ,from the discharge of the pump to the flow measuring location (hose nozzle).

Am I right to assume that we must make sure that the pump and water source can deliver such a pressure at the 150% flow?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources