im currently working on route 405 project and we need to build temporary shoring. i have asked a lot of companies but no one seems to have MC 18x 58 sections to be used as walers for tiebacks. can i use W 18x46 section which has almost the same section modulus if i dont find MC 18x58? or else what should be my other option to cop with this problem?





RE: Tieback Walers
Section substitutions happen all the time, but they have to be approved by the designer, specially if the section properties are smaller than those on the section specified.