Concrete Beam Design
I've been asked to look at designing a concrete beam that varies in cross-sectional dimensions. Essentially it has a flat and level top surface while the bottom surface is a shallow arch which results in a reduced beam depth towards mid-span. Would this configuration be analyzed as a simply supported beam or an arch? My problem with a shallow arch is that the lateral reactions are huge and I need this to be simply supported. The ends of the beam are restrained. Any thoughts?
RE: Concrete Beam Design
I'd prefer to design it as superficial, but I don't want it to behave in a different manner and have the arch try to spread...
I'm inclined to agree with ToadJones here, unless you have some funky support condition that would necessitate accounting for thrust (I can't really think of any, though)
The beam is simply supported (pinned at both ends) and therefore will be subject to thrust loads if applicable.
Do others concur with frv? I can't seem to come up with a good explanation as to why this would be designed one way over the other.
We are Virginia Tech
Go HOKIES
Case A
This is the beam in question. Does it behave like an arch or like a simple beam? So far undecided.
Case B
This is clearly an arch. The only difference is that it has a little more concrete in the compressive zone at midspan of the beam as opposed to Case A.
Case C
This is clearly a beam. The additional concrete on top of the beam could be assumed as superficial.
Conclusion
To me, it seems that the orientation of the flexural steel is what governs the behavior of the beam. By slightly arching the steel over the span in Case A, you induce some compression into the steel as it is no longer perpendicular to the span. It then becomes a beam-column. This compression is transferred to the pinned supports as thrust. It is interesting to note that the compression will partially offset the tensile forces in the steel resulting from bending, which acts in a similar manner to prestressing.
How does this sound to everyone else?
IMO, none of the cases you show are necessarily an arch.
The thrust can only be developed if the supports are rigid like abutments, if the supports are rigid the thrust will develop not matter what the shape, as long as the stiffness is correct.however to get check if a beam is an arch best to do a strut tie diagram.
An expert is a man who has made all the mistakes which can be made in a very narrow field
Agreed that this is not a classical "arch", but I used the terminology in describing the behavior for lack of a better one.
Rowing,
The supports are definitely rigid and the magnitude of the thrust would need to be calculated if it is an issue. My concern is that from arch theory: the shallower the arch, the higher the thrust. I hadn't thought about the strut-tie on this one as I rarely have the need to use it, but its definitely something to look into.
For a very shallow arch, there is a danger of snap through, in which case the member must be designed as a beam.
BA
Are you sure the supports are rigid, as you have noted the force generate if these are rigid is high. so if the supports are not designed for this force they will deflect and not be rigid, and the arch will be a beam.
I have a feeling that this is a simple problem turned into a science experiment and we are not point this out because we don't have all the information.
Treat the top section as a rectangular beam with straight bars designed for bending.
Provide additional curved bars for temperature and shrinkage.
Just to clarify, you are implying that the primary flexural reinforcement being continued straight through the beam? Then, additional reinforcement be placed on the bottom face to account for shrinkage and crack control?
I was remarking that the solid described when without reinforcement would contain inside the arch as the mechanism of resistance. By adding the rebar, that may follow of course the top and bottom faces for the longitudinal, and the stirrups, we allow the mechanism of Mörsch to form and then design it as a beam.
Of course one could decide to take only part, say a prismatic rectangular inscribed beam, and then hang the rest of the beam as dead weight.
In practice, in the same way than for sloped roofs, the arcing action will develop. Inclined roofs push the walls, and arced beams show inclined reactions on unyielding supports. You can't entirely fool nature by just adding reinforcement. However, once the necessary yield (lateral movement at the support) has occurred to relieve the push, this member if well reinforced as a beam would start to work entirely so.
Note that in the classical way of reinforcing these reinforced concrete beams, even the inclined push of the root corbels or arcing showed, for it was used to reduce the shear at the section, and so contributed to the vertical transmission of the load, then divided in shear and vertical component of the push. My seventies' copy of the reinforced concrete treaty by Montoya, Meseguer, Morán had quantification for the proper relief of shear to be taken when wanting to so account.
I assume in later years it was understood accounting this reduction of the shear due to the push was an unnecessary complication and then all the shear reinforcement was being dimensioned without any reduction from any inclined push. Then, also, only such (the total) shear was contributing as reaction on the column.
The risk with this is that excessive crack widths may develop due to the tensile reinforcement being located too far from the tensile face.
Has post-tensioning the member been discussed?
BA
How is the element supported; Will there be an expansion joint at one end or will it be fixed (horizontally)?
If the flexural reinforcement is provided horizontally at the level h (with allowance for concrete cover), how the the structure be detailed towards the supports?
No cushions will be required. Look at the amount of compression there will be. The thrust for this angle (1/2' in 15' change in centroid)would be enormous, resulting in very high compression stresses and very large shortening in the section, thus creating the snap-thru that you mentioned in your earlier post. If the shortening under compression is more than the length of the centroid - length of the span, then it must snap-thru. Then it is a beam.
Just design it as a beam and forget about the rest. A lot of bridges have been designed with far larger soffit curvatures and arch action is ignored. It is flexural.
The main bars should continue straight as otherwise it would tend to straighten under tension and could spall your cover. Yes these bars will become further and further from the bottom of your beam but so will the stress reduce as you get further away.
The curved bars are provided purely for temperature and shrinkage and will prevent bottom face cracking. These will attract some bending stress but it will be much lower than the main bars.
Additional side face bars may also be required.
How can we make the assessment that the bars further away from the neutral axis will take a lower stress?
The way I see the problem and the acceptable design philosophy as directed by this thread is to design the beam as a prismatic section 3' deep along the entire span. Towards the ends of the spans, smaller bars are provided as face reinforcement to limit cracking.
What other practices are available to limit the cracking to the soffit of the beam where the distance from the flexural reinforcement to the extreme fiber gets close to 1'.
The justification is that bar stress is realted to M/d reduce M and increase d and the stress goes down.
There is also an intermediate stage where both sets of bars will be taking stress.
these things were being designed successfully long before engineers started worrying about crack widths.
You are correct. No cushions are necessary.
csd72,
The use of straight bottom bars is one solution. Curved bars enclosed within ties designed to resist radial stress is another. Personally, I prefer the latter but it is a matter of engineering judgment.
BA
BAretired,
Just to be thorough with this discussion, say the beam was increased in width sufficiently to be be considered a slab. Span, curvature, thickness, etc. remains the same. This would obviously preclude the use of ties from a practicality standpoint. In your opinion, would straight bottom bars be the only solution if this were the case?
Straight bars are also an option. A series of straight bars placed tangent to the curve at three or more points could be considered. They would need to be generously lapped.
BA