NFPA 20 Sensing Lines
2

NFPA 20 Sensing Lines

NFPA 20 Sensing Lines

(OP)
Does the current NFPA 20 allow for the use of flexible tubing or hoses on the pressure sensing lines or are they required to be rigid?

The 2007 NFPA 20 reads: "5.29.3 The pressure-sensing line shall be brass, copper, or series 300 stainless steel pipe or tube, and the fittings shall be of 1/2in (15mm) nominal size."

Would corrugated stainless steel tubing (CSST), or stainless steel hose comply?

RE: NFPA 20 Sensing Lines

The wording in the 2010 edition of NFPA 20 is:

4.30.3* The pressure sensing line shall be brass, rigid copper pipe Types K, L, or M, or Series 300 stainless steel pipe or tube, and the fittings shall be of 1⁄2 in. (15 mm) nominal size.

A.4.30.3 The use of soft copper tubing is not permitted for a
pressure sensing line because it is easily damaged.

Just my thought, but it seems like they need to be rigid piping.   

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: NFPA 20 Sensing Lines

The NFPA does define it has to be ridgid but in fact as Travismack mentioned all piping defined under 4.30.3 are ridgid:
4.30.3* The pressure sensing line shall be brass, rigid copper pipe Types K, L, or M, or Series 300 stainless steel pipe or tube, and the fittings shall be of 1⁄2 in. (15 mm) nominal size.

I believe because of the amount of vibration it needs to be ridgid.

RE: NFPA 20 Sensing Lines

(OP)
Okay, that makes sense.

Thanks for the quick replies!

RE: NFPA 20 Sensing Lines

Also make sure you install individual sensing lines as required.

RE: NFPA 20 Sensing Lines

(OP)
Of course :)

Just looking for ways to simplify installation a bit.

Any suggestions?

RE: NFPA 20 Sensing Lines

I've seen the sensing lines tied in downstream of the pump discharge valve, and with non-supervised block valves in the sensing lines themselves...I would avoid doing that for what should be obvious reasons.

Copper (rigid pipe not tubing) should be cinch to solder  in from the pump to the nearby controller.  A twenty foot stick and a few elbows would do it.  What could be simpler? Something like a braided washing machine hose would physically work, but why spent the big $$ on the pump, controller, dedicated electrical service, fire resistance rated enclosure, etc. and then go cheap on this cheap but important piece.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources