Generator Neutral Short Circuit Current

Generator Neutral Short Circuit Current

Generator Neutral Short Circuit Current

(OP)
I'm working on a generator neutral bus design and I'm wondering what the short circuit current will be at the neutral. I can't find anything in IEEE on this subject. The spec for the isolated phase bus on the line side of the generator is 388kA Assym.  Would the current on the neutral be 388kA/SQRT(3)?

Thanks for any help.
Steve

RE: Generator Neutral Short Circuit Current

In case of a phase to neutral fault, the current in the neutral will be the same as phase current. Ask for or look up for that value for your project. Some has done the fault analysis.

Rafiq Bulsara
http://www.srengineersct.com

RE: Generator Neutral Short Circuit Current

Assuming the generator is impedance grounded, the fault current for a phase to ground fault will return through the neutral impedance, so if you know that impedance you can figgure the fault current. Usually this value is less than the normal current during production.

Rarely have I seen a neutral braced for phase to phase faults of three phase faults, which I attribuite to the thinking isolated phase bus can't fail anyway but phase to ground.

However, does anyone know what happens to the phases once they enter the GSU, or aux. transformer?

RE: Generator Neutral Short Circuit Current

(OP)
Thanks for the quick response on my question.  

rbulsara: What do you mean by "phase to neutral fault".

One thing I need to add... This is a generator neutral tie with all three bushings tied together with one copper conductor. It is 35,000A forced cooled and has a neutral grounding cubicle connected to the neutral tie.

cranky108: When we terminate isolated phase bus to the the GSU, it is in a segregated box so the fault would also be pahse to ground.
 

RE: Generator Neutral Short Circuit Current

Exactly what it reads. When would a fault current will flow through the neutral?

Rafiq Bulsara
http://www.srengineersct.com

RE: Generator Neutral Short Circuit Current

Phase to phase fault current will flow through the neutral bar which bonds the neutral ends of the three windings, as dictated by Kirchoff's Rule. In that respect the bonding bar must be braced for the maximum fault. The connection between neutral and earth only needs to be heavy enough for the maximum line-earth fault, which on a big set is normally less than 10A or so. Normally the smallest available MV cable is capable of carrying much larger current.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources