Lost - NFPA 13 2002 edition versus 2007 edition

Lost - NFPA 13 2002 edition versus 2007 edition

Lost - NFPA 13 2002 edition versus 2007 edition

(OP)
OK, I confess that I am not as comfortable navigating the 2007 edition of NFPA 13. With that said, I need help locating a requirement for the protection of palletized storage of plastics and rubber.

In the 2002 edition, Section 12.2.3.1.5.2 specified that when the clearance between sprinklers and the storage exceeded 20 feet, protection is required so the clearance is limited to 20 feet or less.

When I look in Section 15.1.2, it appears this section was deleted. Was it actually deleted, or was it relocated? If it was relocated, where did it end up landing?

I'm asking because FM still has the requirement and I'm aware of the problems associated with excessive sprinkler clearances.

Thank you in advance for your assistance.

RE: Lost - NFPA 13 2002 edition versus 2007 edition

Stookey:

I believe what you are looking for is found in Chap 12 under general storage requirements:

12.1.3.4* Ceiling Height.
12.1.3.4.1 For ceiling heights that exceed 30 ft (9.14 m),
where the distance between the ceiling height and top of storage exceeds 20 ft (6.1 m), protection shall be provided for the storage height that would result in a 20 ft (6.1 m) distance between the ceiling height and top of storage.
12.1.3.4.2 The requirements of 12.1.3.4 shall not apply to
storage arrangements protected in accordance with Chapter
13, Miscellaneous Storage.

 

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: Lost - NFPA 13 2002 edition versus 2007 edition

(OP)
Thank you Travis. I've been flipping code pages for the past 90 minutes trying to find this.

I appreciate your assistance.

RE: Lost - NFPA 13 2002 edition versus 2007 edition

The electronic version with a key word search is a great thing!  Glad I could help my friend!

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: Lost - NFPA 13 2002 edition versus 2007 edition

wow, friends helping friends...so cool

spkreng, CET

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources