Cantilevered Masonry Wall
All:
Are there any specific things to watch out for when designing a 10' deep masonry wall/beam cantilevering out 6' picking up 44 kips at the end?
We have an odd situation where a building's facade sticks out and one of the ideas was to extend an already existing masonry wall and use it as a deep beam rather than pour concrete. The facade is used to hide rooftop equipment and the back walls form the equipment room.
I am designing reinforcing bars to carry all the shear and fully grouting the wall. How far beyond the cantilever should I extend my full grouted cells?
We are Virginia Tech
Go HOKIES
RE: Cantilevered Masonry Wall
In concrete you have fifty "b", but masonry does not address the issue. It is possible that the allowable masonry stresses are so low that it is not an issue, but it maybe something you wish to consider.
Also, what is equipment room framing? Are steel joists creating the floor area? Make sure to have enough depth so that the framing does not want to break out of the bottom of the beam.
Is the wall taking out-of-plane loads? It would have to be a case you need to check. Also, if the facade acts as a parapet you zone 2 areas have zone 4 pressures downward. So it may add to the load you are trying to carry.
In masonry, it is 32b for unbraced compression flange.
The equipment room is really only to host cooling towers. No roof over it. Just a wall around its 4 sides.
Go HOKIES
BA